RH Testing For Parking Garages
07-12-2012, 09:00 AM,
#4
RE: RH Testing For Parking Garages
I would ask the manufacturer for their requirements first. If the coating is quite breathable they may be rather lax in their demands.

Typically though almost any finish requires some degree of dryness be inherent in the substrate. You wouldn't put ceramic tile on a 2 day old slab, but 30 days may be fine.

Determining the dryness is rather easy if the slab reaches a temperature conducive for testing. If the concrete never falls below 90 degrees, the rH can read quite low, yet the moisture present could be rather high. Likewise in the winter a cold slab would read artificially low. This is why we test at a standard expected temperature. Outside that range is going to be very wide spread, but you may get a good idea of comparable rH if you can read the slab around 70 degrees.

If the temperature is moving quickly, you may need to insure your probe and the sensor are acclimated also. Can you shade the area you are reading?
JD Grafton
Concrete Answers for Flooring Problems
[email protected]