RH Testing Lighweight Concrete
What are the procedures for testing Lightweight Concrete, and can you get a true reading.
|
|||
|
09-22-2009, 03:42 PM
Post: #2
|
|||
|
|||
|
RE: RH Testing Lighweight Concrete
ASTM F2170. I don't see why you wouldn't get a true reading when following that method.
|
|||
|
09-24-2009, 04:10 PM
Post: #3
|
|||
|
|||
|
RE: RH Testing Lighweight Concrete
What is the thickness of lightweight concrete? Anyone know?
|
|||
|
09-28-2009, 05:24 AM
Post: #4
|
|||
|
|||
|
RE: RH Testing Lighweight Concrete
The thickness is 6"
|
|||
|
12-16-2009, 12:05 PM
Post: #5
|
|||
|
|||
|
RE: RH Testing Lighweight Concrete
Lightweight is scary! The aggregate is very porous and as such holds a great amount of water. Drying time for lightweight concrete can be 300% longer than standard concrete. I'd figure 3 months per inch of thickness and go from there.
I had a job that was on 11" of lightweight and I had MVER readings of 3lbs - 4lbs, with RH readings of 96%. The floor failed after the first year (that's when I was called in) and we ended up coating the floor with a Moisture Mitigation System. JD Grafton Concrete Answers for Flooring Problems JGrafton@ccsolves.com |
|||
|