Thread Rating:
  • 3 Vote(s) - 4.33 Average
  • 1
  • 2
  • 3
  • 4
  • 5
Moisture Meters
09-11-2008, 09:00 AM, (This post was last modified: 09-11-2008, 04:12 PM by hnelson.)
#1
Moisture Meters
I have heard that a surface moisture meter is not as good a way to measure moisture in concrete as using an internal relative humidity sensor. Could someone clarify this for me?
Quote this message in a reply
09-12-2008, 01:28 PM,
#2
RE: Moisture Meters
Blake,
Correct, surface moisture meters and surface testing measures the very top of the concrete. As concrete dries from the top down, the slab may be wet at the bottom while indicating dry at the surface. Once a slab is covered with a moisture sensitive flooring the slab will go into equilibrium and the moisture will increase at the surface. The use of a RH Sensor will measure the internal moisture at the apex of the drying curve, which is the point where equilibrium crosses.
Please advise any questions
Rayt
Quote this message in a reply
09-12-2008, 05:42 PM,
#3
RE: Moisture Meters
Thanks, and how deep should I measure to get to the equilibrium point?

Blake
Quote this message in a reply
09-15-2008, 04:19 PM,
#4
RE: Moisture Meters
ASTM F-2170 recommends 40% the thickness of the slab
Rayt
Quote this message in a reply
10-21-2008, 11:49 AM,
#5
RE: Moisture Meters
Blake,
About 40% the thickness of the slab. 4" slab about 1-1/2 - 1-3/4"
Rayt
Quote this message in a reply


[-]
Share/Bookmark (Show All)
Facebook Twitter Linkedin Technorati Digg MySpace Delicious