RH Testing Lighweight Concrete - JDJR - 09-21-2009 05:59 AM

What are the procedures for testing Lightweight Concrete, and can you get a true reading.


RE: RH Testing Lighweight Concrete - Ben - 09-22-2009 03:42 PM

ASTM F2170. I don't see why you wouldn't get a true reading when following that method.


RE: RH Testing Lighweight Concrete - Ernesto - 09-24-2009 04:10 PM

What is the thickness of lightweight concrete? Anyone know? Smile


RE: RH Testing Lighweight Concrete - JDJR - 09-28-2009 05:24 AM

The thickness is 6"


RE: RH Testing Lighweight Concrete - CC Solutions - 12-16-2009 12:05 PM

Lightweight is scary! The aggregate is very porous and as such holds a great amount of water. Drying time for lightweight concrete can be 300% longer than standard concrete. I'd figure 3 months per inch of thickness and go from there.

I had a job that was on 11" of lightweight and I had MVER readings of 3lbs - 4lbs, with RH readings of 96%. The floor failed after the first year (that's when I was called in) and we ended up coating the floor with a Moisture Mitigation System.