Rrozema:

1) Having a copy of the ASTM F2170 standard for which the Rapid RH was designed to meet, is a must. Have you ever been given one? I find the answer to this to be no more times than not when I talk to people. This should not be on you.

2) I have a hard time believing that the pour on this pan is this shallow. Usually the shallow part would be around this deep but not the deep section of the pan. With that being said, alot of people will cut the top of the barrel off on shallow pours such as gypsum where it is being used for soundproofing.

3) Determining whether 20% or 40%-Is the slab drying from one or two sides? Any pan decking on the market, even "vented" decking, is only drying from one side, thus 40% is required. The easiest way to determine whether the slab is open on the bottom is go to the lower level and look up. Can you see concrete or corrugated metal?

Hope this helps!

Jason
Find all posts by this user
Quote this message in a reply
Post Reply 


[-]
Share/Bookmark (Show All)
Facebook Twitter Linkedin Technorati Digg MySpace Delicious

Messages In This Thread
improper probe depth - Rrozema - 02-23-2012, 01:00 PM
RE: improper probe depth - rapidrhrep - 02-23-2012 01:51 PM
RE: improper probe depth - Rrozema - 02-23-2012, 02:22 PM
RE: improper probe depth - Rrozema - 02-28-2012, 08:44 AM
RE: improper probe depth - rapidrhrep - 03-01-2012, 07:43 AM
RE: improper probe depth - CC Solutions - 03-01-2012, 12:47 PM
RE: improper probe depth - Rubensgt40 - 03-04-2012, 03:56 PM
RE: improper probe depth - CCR - 03-09-2012, 06:14 AM
RE: improper probe depth - GP-CA - 03-23-2012, 02:24 PM
RE: improper probe depth - Ernesto - 03-23-2012, 07:51 PM
RE: improper probe depth - CC Solutions - 03-24-2012, 06:12 AM