RH and MVER Concrete Moisture Conversion table

#1
I found this conversion chart on a blog and wondered if anyone else had seen this and if it's accurate?

"<75% would be equivalent to <3 lbs/sf
76%-85% would be equivalent to 3-6 lbs/sf
86%-90% would be equivalent to 6-12lbs/sf
>91% we are going to want to look very closely at the floor before moving forward"

I found it at this blog: http://www.florock.net/blog/2010/06/09/concrete-floor-coating-2010
Reply

#2
It is not accurate. The numbers are not compatible. They measure different things and IMHO ASTM 1869 doesn't provide a valid test to start with. It is just the best option available. Run a cal cl test on a piece of glass. You'll see.

There is a reason Perm Ratings are done with ASTM E96 not F1869.
Reply

#3
There is NO CORRELATION between RH and MVER.

Think of it this way:

You have a dry slab, 50 years old, suspended, RH is 55%.
You wet that slab for 24 hours, flood it.
The slab RH is still 55%, the surface water soaked in 1/4" to 1/2" or so.
A CaCl test will read about 12lbs placed on that wet surface.

Conversely a slab in a very dry building laying on a wet subsoil can read 3lbs MVER because the surface is very dry, but the lower portion of the slab is very wet. RH readings can easily reach 90%+. Cover that slab with a moisture sensitive flooring and the concrete will continue to absorb water and RH will climb even higher.

I have personally seen these scenarios, they are very real.

JD Grafton
Concrete Answers for Flooring Problems
[email protected]
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Moisture going up Rubensgt40 3 1,816 07-05-2014, 03:18 AM
Last Post: Rubensgt40
  ICRI pH testing Concrete Repair Bulletin eaadams 4 2,752 05-20-2014, 12:00 PM
Last Post: Ashok Kakade
  35-40 year old concrete with moisture problems Tscdad 13 8,085 05-19-2014, 10:55 AM
Last Post: eaadams
  Digital moisture meter QC worker 2 2,042 05-10-2014, 08:07 PM
Last Post: Rubensgt40
  Concrete Hood Method Blake McFee 9 27,708 11-08-2013, 01:41 PM
Last Post: eaadams
  Tandus removes moisture testing requirement eaadams 2 4,304 09-27-2013, 10:26 AM
Last Post: eaadams
  RH in Concrete for Wood Floor with Vapor Membrane eaadams 35 65,337 05-01-2013, 07:20 AM
Last Post: jim decker
Question Concrete Cork Sandwich Floor System JKJeremy 4 8,431 01-30-2013, 04:43 PM
Last Post: eaadams
  Carbide moisture testing CC Solutions 4 8,874 09-18-2012, 06:11 PM
Last Post: CC Solutions
  We're almost at 3lbs MVER, so what if the rH is over 90% ? CC Solutions 27 42,767 08-19-2012, 04:11 PM
Last Post: Rubensgt40

Digg   Delicious   Reddit   Facebook   Twitter   StumbleUpon  


Users browsing this thread:
1 Guest(s)