(10-14-2012, 09:55 AM)CC Solutions Wrote:  Being that slabs dry to the top, you could drill down until you hit a point that exceeds the maximum level of RH and stop there.

I'm just saying it is easy to drill to 4" and check what you have. If it is too high, it will only get higher as you drill further down.

If you want to remove the top few inches of concrete to get your sensor down 6" I can't see how that would affect a short term reading.

On the other hand, if you do not drill down to the required depth, and your reading is low, your just wasting your time and a sensor.

Stephen Perrera dba
Top Floor Installation Co.
http://www.tucsonazflooring.com
http://www.floorsavior.com

10-24-2012, 08:08 AM #22
rapidrhrep Concrete Moisture Tutor **
Status: Offline Posts:85 Threads:3 Joined:Aug 2011
Another thing to keep in mind with all of this is that many experts will tell you that any slab in excess of 12" many never dry naturally to an acceptable level for finished floor products. Dimensionally, this is why the Rapid RH is the size it is i.e. it can do 40% of a 12" slab. This being said, this is why many people do as is being spoken here, they do the max depth they comfortably can with the Rapid RH. I can tell you, I have had people who have gone to the extremes and drill, clean, and insert deeper than that. Human creativity never ceases to amaze me.Smile

Jason

11-20-2012, 03:18 PM #23
CCR Concrete Moisture Coach ***
Status: Offline Posts:236 Threads:14 Joined:Dec 2011
THICK SLAB UPDATE:

Called back 2 weeks ago to get new readings. Guess what? Bingo!!! They're still in the mid to upper 90s. At this point, the manufacturer (or someone) had approved the use of a well known epoxy-based mitigation, and I assume they will be moving ahead with prep and application...wrong!

So they have the installer place 3 Cal. Clhor. kits in a 8,000+ sf area and they get levels of 2-3 lbs. Don't know if they even bothered grinding this black, slick, hard, power trowled surface.

Now they're going to shot blast the surface and wait. Hope they plan on being there awhile because that slab is never going to dry. But why take my word for it?Huh

But this is what kind of amazed me...the GC said that the Wagner RH tended to provide "conservative readings", meaning (to me), that they were purposely calibrated to provide high readings. I responded that doing so would not only be unethical on Wagner's part, but would make thousands of tests invalid by ASTM standards. The subject stopped there.

People never cease to amaze me.

JK Nixon
Concrete Restoration Services, LLC
Pittsburgh, PA
http://www.rhtester.com

11-20-2012, 03:28 PM #24
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,067 Threads:69 Joined:Dec 2009
Opening the surface will promote drying. Instead of taking about 4 years to dry, that slab could be dry in one year now if conditions are perfect!!! Tongue

The low CaCl readings on WET slabs are EXACTLY why 1869 was changed, and 90% of the reason the flooring industry is struggling now. Sure that glass finish is allowing very little vapor out, but the slab is a time bomb waiting to ruin some installer's life!
And I know it's not porous... What do the installation instructions say about installing over a non-porous substrate? Do installers follow those instructions? Not likely.

Low VOC adhesives are just part of the new issues we face. How about ginormous power trowel finishing machines???

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com

11-20-2012, 03:43 PM #25
CCR Concrete Moisture Coach ***
Status: Offline Posts:236 Threads:14 Joined:Dec 2011
The slab is 19 months old, and it will never, ever dry. I keep telling them this and they won't accept it. They're installing a static disipating, heat welded floor made by a well known manufacturer who is known to make premium, yet tempermental floor coverings.

They have a very good sf price for prep and application of the moisture system but don't want to spend the money.

Right now, I blame the architect AND the GC for not knowing enough about concrete to have 1). specified a more open, porous finish and 2). not including a contingency spec and price for a moisture mitigation system.

JK Nixon
Concrete Restoration Services, LLC
Pittsburgh, PA
http://www.rhtester.com

11-20-2012, 05:21 PM #26
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,067 Threads:69 Joined:Dec 2009
I agree the architect and the GC should have known from the get-go that the floor had to have good conditions to dry. Then when they burned the snot out of it they should have known for sure it wasn't going to dry unless it was opened up so it could breathe.

The truth is, I bet they are both shaking their head blaming the flooring installer for the problem....

And what is the first letter of the flooring manufacturer's name?

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com

11-20-2012, 05:26 PM #27
eaadams Concrete Moisture Expert *****
Status: Offline Posts:600 Threads:88 Joined:Jul 2010
AAAAAnyones guess, TTTTTsk TTTTTsk on those who guees wrong

11-20-2012, 05:30 PM #28
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,067 Threads:69 Joined:Dec 2009
Nope... CCR PM'd me... Your guess is way out in left field....

The slab must be cast in place, so I assume it can dry from below....

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com

11-20-2012, 05:33 PM #29
CCR Concrete Moisture Coach ***
Status: Offline Posts:236 Threads:14 Joined:Dec 2011
Yup. Isolated and from surrounding slabs and
engineered to take extra heavy loads.

JK Nixon
Concrete Restoration Services, LLC
Pittsburgh, PA
http://www.rhtester.com

11-20-2012, 05:35 PM #30
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,067 Threads:69 Joined:Dec 2009
Heavy loads = lots of stress on that floor system.... No time for a weak substrate!

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com








Possibly Related Threads...
Thread / Author Replies / Views Last Post
4 Replies 8,677 Views
Last Post by Ashok Kakade
05-20-2014, 12:00 PM
4 Replies 10,514 Views
Last Post by CC Solutions
12-20-2013, 10:23 PM
2 Replies 8,346 Views
Last Post by eaadams
09-27-2013, 10:26 AM
21 Replies 66,849 Views
Last Post by CCR
07-19-2013, 05:14 PM
51 Replies 122,097 Views
Last Post by ILLENTINC
11-19-2012, 11:59 AM
4 Replies 13,217 Views
Last Post by CC Solutions
09-18-2012, 06:11 PM
22 Replies 48,785 Views
Last Post by Ernesto
07-30-2012, 07:01 PM
62 Replies 125,484 Views
Last Post by CC Solutions
12-07-2011, 07:27 AM
36 Replies 90,937 Views
Last Post by CC Solutions
04-19-2011, 04:59 PM
9 Replies 27,526 Views
Last Post by CC Solutions
04-05-2011, 05:33 AM

Users browsing this thread:
1 Guest(s)