Lightweight is scary! The aggregate is very porous and as such holds a great amount of water. Drying time for lightweight concrete can be 300% longer than standard concrete. I'd figure 3 months per inch of thickness and go from there.

I had a job that was on 11" of lightweight and I had MVER readings of 3lbs - 4lbs, with RH readings of 96%. The floor failed after the first year (that's when I was called in) and we ended up coating the floor with a Moisture Mitigation System.

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com








Messages In This Thread
RH Testing Lighweight Concrete - JDJR - 09-21-2009, 05:59 AM
RE: RH Testing Lighweight Concrete - Ben - 09-22-2009, 03:42 PM
RE: RH Testing Lighweight Concrete - Ernesto - 09-24-2009, 04:10 PM
RE: RH Testing Lighweight Concrete - JDJR - 09-28-2009, 05:24 AM
RE: RH Testing Lighweight Concrete - CC Solutions - 12-16-2009, 12:05 PM

Possibly Related Threads...
Thread / Author Replies / Views Last Post
4 Replies 5,189 Views
Last Post by Ashok Kakade
05-20-2014, 12:00 PM
13 Replies 13,484 Views
Last Post by eaadams
05-19-2014, 10:55 AM
9 Replies 31,093 Views
Last Post by eaadams
11-08-2013, 01:41 PM
2 Replies 5,888 Views
Last Post by eaadams
09-27-2013, 10:26 AM
35 Replies 73,685 Views
Last Post by jim decker
05-01-2013, 07:20 AM
4 Replies 9,946 Views
Last Post by eaadams
01-30-2013, 04:43 PM
33 Replies 56,264 Views
Last Post by eaadams
11-21-2012, 10:19 AM
51 Replies 97,022 Views
Last Post by ILLENTINC
11-19-2012, 11:59 AM
4 Replies 10,377 Views
Last Post by CC Solutions
09-18-2012, 06:11 PM
22 Replies 39,219 Views
Last Post by Ernesto
07-30-2012, 07:01 PM

Users browsing this thread:
1 Guest(s)