RH Test Hole Callout

#4
(09-26-2008, 09:40 AM)Ben Wrote:  I'm following the spec to put a test hole in the slab every 1000 sq ft after putting 3 test holes in the first 1000 sq ft. What is the rational for the 1000 sq ft callout?

Ben,
The rational for testing for every 1,000 s/f is; it represents the amount of concrete per truck load. A truck load of concrete will cover approximately 800 - 1,000 s/f 4-inches thick.
Regards
Rayt
Reply


Messages In This Thread
RH Test Hole Callout - Ben - 09-26-2008, 09:40 AM
RE: RH Test Hole Callout - rthompson - 09-26-2008, 01:58 PM
RE: RH Test Hole Callout - CMoore - 10-27-2008, 08:21 AM
RE: RH Test Hole Callout - rthompson - 11-04-2008, 10:03 AM

Possibly Related Threads...
Thread Author Replies Views Last Post
  Test Before You Spec! CCR 6 8,618 05-13-2013, 04:51 PM
Last Post: Ernesto
  Cal Chlor Test CCR 10 15,871 01-18-2013, 04:48 PM
Last Post: eaadams
  Another tester brought in to dispute test results. CC Solutions 4 9,855 08-14-2011, 09:32 PM
Last Post: CC Solutions
  Interesting Test Result eaadams 16 30,535 08-08-2011, 11:41 AM
Last Post: CC Solutions
  How to test RH levels after moisture barrier is used DShenk 3 10,784 08-30-2010, 12:42 PM
Last Post: Ernesto
  Old Slab Test eaadams 5 12,362 07-12-2010, 07:00 PM
Last Post: Ernesto
  pH test eaadams 2 7,998 07-09-2010, 09:45 AM
Last Post: eaadams
  Test time for RH test jigar0896 14 31,907 01-15-2010, 09:36 PM
Last Post: CC Solutions
  When to Test CFI 2 8,776 12-16-2009, 11:45 AM
Last Post: CC Solutions
  creating the hole for the sensor SDJeff 1 6,998 11-09-2009, 04:39 PM
Last Post: Ben

Digg   Delicious   Reddit   Facebook   Twitter   StumbleUpon  


Users browsing this thread:
1 Guest(s)