#Login Register
RH Numbers Rising
  • 0 Vote(s) - 0 Average


04-11-2011, 09:54 AM #31
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,065 Threads:69 Joined:Dec 2009
One of Bruce's old articles. I wonder how he figured that number out? Maybe by weighing a jar of sand and then a flooded jar of sand and extrapolating the number?

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com

04-11-2011, 08:50 PM #32
Ernesto Concrete Moisture Expert *****
Status: Offline Posts:606 Threads:33 Joined:Sep 2009
There must be some sort of algorithm for that.

Stephen Perrera dba
Top Floor Installation Co.
http://www.tucsonazflooring.com
http://www.floorsavior.com

04-18-2011, 12:26 PM #33
T_Schneider Newbie *
Status: Offline Posts:7 Threads:0 Joined:Mar 2011
COD, I realize I am showing up very late to this party, but I did want to point out that ASTM F2170 requires the space to be acclimated (HVAC on) prior to testing for relative humidity. This may have been skewing your data.

Regards,

T. Schneider
ARDEX Engineered Cements

04-18-2011, 01:10 PM #34
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,065 Threads:69 Joined:Dec 2009
(04-18-2011, 12:26 PM)T_Schneider Wrote:  COD, I realize I am showing up very late to this party, but I did want to point out that ASTM F2170 requires the space to be acclimated (HVAC on) prior to testing for relative humidity. This may have been skewing your data.

Regards,

T. Schneider
ARDEX Engineered Cements

Technically nowhere in the ASTM does it say the space must have the HVAC on.

We wouldn't want testers thinking they cannot conduct accurate RH testing just because the HVAC is not on. In 99% of all the hospitals I work in, the HVAC is not commissioned until a few days before the building is turned over.

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com

04-18-2011, 01:20 PM #35
T_Schneider Newbie *
Status: Offline Posts:7 Threads:0 Joined:Mar 2011
OK, I stand corrected, it does not specifically mention HVAC, but it does say that the concrete must be "at service temperature" and that the air space above the concrete "shall be at service temperature and service relative humidity." Both of these are stipulated "for at least 48 hours before making relative humidity measurements in the concrete slab." IMO, HVAC is strongly implied by this, unless you happen to be having a string of lovely, 72-degree and 0% humidity days. If that happens often where you are, tell me where you live - I'm moving! Smile

04-18-2011, 01:28 PM #36
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,065 Threads:69 Joined:Dec 2009
Well let's consider service temperature.... ASTM F1869 has the same wording yet also adds that temperatures between 65F and 85F and Rh in the 40% to 60% range is acceptable. I think we can all agree that RH probes are less susceptible to temperature fluctuations than MVER testing equipment.

But I'll make my point with this: Most job sites will be under temporary conditioning when new construction is being conducted. This temporary heating and cooling can and does provide adequate testing climates for RH testing. Limiting testing to a time when HVAC is active is not practical on commercial jobs. Big Grin

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com

04-18-2011, 03:08 PM #37
Ernesto Concrete Moisture Expert *****
Status: Offline Posts:606 Threads:33 Joined:Sep 2009
(04-18-2011, 01:20 PM)T_Schneider Wrote:  OK, I stand corrected, it does not specifically mention HVAC, but it does say that the concrete must be "at service temperature" and that the air space above the concrete "shall be at service temperature and service relative humidity." Both of these are stipulated "for at least 48 hours before making relative humidity measurements in the concrete slab." IMO, HVAC is strongly implied by this, unless you happen to be having a string of lovely, 72-degree and 0% humidity days. If that happens often where you are, tell me where you live - I'm moving! Smile

Pick a county TSchneider. We are a close as your gonna get.Cool

http://www.usairnet.com/weather/maps/current/arizona/relative-humidity

http://www.usairnet.com/weather/maps/current/arizona/temperature


Stephen Perrera dba
Top Floor Installation Co.
http://www.tucsonazflooring.com
http://www.floorsavior.com

04-18-2011, 04:46 PM #38
eaadams Concrete Moisture Expert *****
Status: Offline Posts:591 Threads:85 Joined:Jul 2010
I just had a GC in Los Angeles tell me they can't get the building acclimated because they can't get heat on until they get the occupancy permit and cant get occupancy permit until flooring is done ....

sounds crazy to me.

04-18-2011, 04:55 PM #39
Ernesto Concrete Moisture Expert *****
Status: Offline Posts:606 Threads:33 Joined:Sep 2009
Yea, they try that here as well. But I checked with the local power company and they said you can get a temporary permit.

Stephen Perrera dba
Top Floor Installation Co.
http://www.tucsonazflooring.com
http://www.floorsavior.com

04-18-2011, 05:15 PM #40
CC Solutions Concrete Moisture Evangelist *******
Status: Offline Posts:1,065 Threads:69 Joined:Dec 2009
There are portable HVAC units to heat and cool buildings, but the GC doesn't want the cost. I wish they could understand the importance of maintaining correct conditions during flooring installation. Sad

JD Grafton
Concrete Answers for Flooring Problems
JGrafton@ccsolves.com








Users browsing this thread:
1 Guest(s)